FYI new cables are 149.95 from amazon.ca
Note these are 8ga cables but a lower temp rating for RV which rates it for 40amps 50amps can be done just watch for the cable getting warm for a short period. I did the research when I bought the Primeweld as it listed 50amps. They said unless you are running full power 100% ha ha ha that the only time you'll really need to be concerned.
I keep it simple and safe, read the spec of the machine, do the math and finally call the manufacturer.Century Wire and Cable Pro-Grip 50' Welding Extension Cord
The heavy duty grounded Pro Grip Welding Extension Cords right angle is designed for use with portable welding machines of 400 Amps or less.www.kmstools.com
I thought $120 is pretty reasonable compared to KMS
Is “welding cable” made to a different spec than similar gauge automotive wiring or house wiring? There seems to be a bunch more strands of copper in welding cable?thats ok for 120$ for sure, I have a few of them, they are ok in the garage (and that's where mine stay) where you dont have to lug them around, but they are seriously over kill unless you are powering 350-400a machine, although nothing wrong with overkill
coming from experience 10awg is the more common size for a welding extension cord for a 200-250a machine going hundreds of feet, even the 300a+ shop machines are usually fed with 10awg (although usually only 20 or so feet), yes i am referring to single phase
I dont think most of you are aware that unless electrical codes have changed the required conductor size to feed a welding machine is not the same as it is for other appliances due to the duty cycle, if there are any electricians in the group with access to the cec for this year they can confirm that this is still the case in 2022/2023
Here is the excerpt ;
42-006 Supply conductors
(1) The supply conductors for an individual transformer arc welder shall have an ampacity of not less than the
value obtained by multiplying the rated primary current of that welder in amperes by a factor of
(a) 1.00, 0.95, 0.89, 0.84, 0.78, 0.71, 0.63, 0.55, or 0.45 for welders having a duty cycle of 100, 90, 80,
70, 60, 50, 40, 30, and 20% or less respectively; or
(b) 0.75 for a welder having a time rating of 1 h.
(2) The supply conductors for a group of transformer arc welders shall have an ampacity not less than the sum
of the currents determined for each welder in the group in accordance with Subrule (1) multiplied by a
demand factor of
(a) 100% of the two largest calculated currents of the welders in the group; plus
(b) 85% of the third largest calculated current of the welders in the group; plus
(c) 70% of the fourth largest calculated current of the welders in the group; plus
(d) 60% of the calculated currents of all remaining welders in the group.
(3) Lower values than those given in Subrule (2) shall be permitted in cases where the work is such that a high
operating duty cycle for individual welders is impossible.
So for example @Degen 's Primeweld 225 at max output on stick (highest current draw) draws 38.1a, but given then 40% duty cycle you multiply 38.1 by .63, so by that math you only need a conductor capable of carrying 24a.....a 10awg
Is “welding cable” made to a different spec than similar gauge automotive wiring or house wiring? There seems to be a bunch more strands of copper in welding cable?
Do the extra strands conduct more amperage? Or is it just for flexibility?Yes. The main difference is flexibility. House wiring isn't very flexible. Automotive is, but not nearly to the extent that a cable is.
I guess I should add abrasion protection, usable temperature range, fire retardant, insulation, etc etc.Is “welding cable” made to a different spec than similar gauge automotive wiring or house wiring? There seems to be a bunch more strands of copper in welding cable?
The strands do change conductivity but not significantly at regular frequencies. It's mainly ability to drag it around, coil it, etc.Do the extra strands conduct more amperage? Or is it just for flexibility?
Gotcha. I made a set of booster cables years ago out of 4 gauge welding cable, 20 feet long I think. They are the cats meowT
The strands do change conductivity but not significantly at regular frequencies. It's mainly ability to drag it around, coil it, etc.
Gotcha. I made a set of booster cables years ago out of 4 gauge welding cable, 20 feet long I think. They are the cats meow
Ya, the cheap booster cables are low strand or even solid wire. Nothing beats really good cable.
But my main bitch is crappy clamps. It's not easy to find good ones.
Yes Canadian Code....annoyed emoji.....spent 10 years in the elevator industry...,,electrical code, building code, elevator code all rest, part of what was second nature just to do the job.@Degen Your realize you are arguing with Canadian electrical code right ? Im quite sure the electrical engineers that wrote the code did the testing to confirm what was acceptable, not to mention that is not anything new, that has been the code for at least 18 years
@Chicken lights welding extension cords are just regular cords, welding cable does have a higher strand count
Yes Canadian Code....annoyed emoji.....spent 10 years in the elevator industry...,,electrical code, building code, elevator code all rest, part of what was second nature just to do the job.
Just a bit of background, currently doing RF engineering and am one the distributer of wire and cable and can get whatever information I need directly from suppliers and manufacturers.
Nonmotor Generator | Motor Generator | |
---|---|---|
Duty Cycle | Multiplier for Arc Welders | |
100 | 1.00 | 1.00 |
90 | 0.95 | 0.96 |
80 | 0.89 | 0.91 |
70 | 0.84 | 0.86 |
60 | 0.78 | 0.81 |
50 | 0.71 | 0.75 |
40 | 0.63 | 0.69 |
30 | 0.55 | 0.62 |
20 or less | 0.45 | 0.55 |