Elektrishun
Ultra Member
Yes, makes sense.Yes and yes.
OK.
Original panel 100A service with ground to a post in the concrete by the copper drain pipe. Also copper wire running from a second ground post (under the breaker panel) to the water pipe which was copper going through the wall before PEX. For all we know there's a connection along that wall under the concrete between the two.
Now we have a brand new 200A service which included new wires from the pole. I buried one of those large ground plates into the earth as per code. That plate wire connects to the wire you see above the PEX valve but also runs parallel to the wire that went to the original post.
However that new ground terminates inside the 200A service box again as per code.
The 200A service box supplies, through a 100A breaker, power to the original 100A panel and now provides the ground to it too. The connection to the original post in the concrete floor by the copper drain pipe was disconnected as there was no evidence that it was even useful.
The one thing I did not photograph when the perimeter drain tile was redone is what they did with the plate. It was hanging from the wire but whether they buried it horizontally or vertically I don't know.
Does that all make sense?
I was wondering about your installation because the PEX would obviously nullify the use of the water line as a ground rod because of where the ground conductor is clamped. Since you have a ground plate buried outside that should take care of establishing an earth ground for all your electrical equipment. Sounds like that second ground rod in the concrete floor, which you stated is connected ("bonded") to the main copper water line, is still used as a ground rod, too.
Last question, only because I am curious about these things, the neutral terminal bar and ground terminal bar in the old panel would have been originally "common" to each other with a "bonding" screw. Now that the old panel has become a sub-panel fed from the new 200A service that screw has been removed - correct?