• Scam Alert. Members are reminded to NOT send money to buy anything. Don't buy things remote and have it shipped - go get it yourself, pay in person, and take your equipment with you. Scammers have burned people on this forum. Urgency, secrecy, excuses, selling for friend, newish members, FUD, are RED FLAGS. A video conference call is not adequate assurance. Face to face interactions are required. Please report suspicions to the forum admins. Stay Safe - anyone can get scammed.
  • Several Regions have held meetups already, but others are being planned or are evaluating the interest. The Calgary Area Meetup is set for Saturday July 12th at 10am. The signup thread is here! Arbutus has also explored interest in a Fraser Valley meetup but it seems members either missed his thread or had other plans. Let him know if you are interested in a meetup later in the year by posting here! Slowpoke is trying to pull together an Ottawa area meetup later this summer. No date has been selected yet, so let him know if you are interested here! We are not aware of any other meetups being planned this year. If you are interested in doing something in your area, let everyone know and make it happen! Meetups are a great way to make new machining friends and get hands on help in your area. Don’t be shy, sign up and come, or plan your own meetup!

Tips/Techniques Thermal overload relay

Tips/Techniques
Working on setting up my diy phase converter. Legs are balanced. Pony runs smooth. The issue I am tracking down is the thermal overload relay tripping. It now takes about 3 mins to trip and cut power to the machines and used to trip out in 30 seconds or less.

I will assume the relay is stock. It only adjusts to 4amps but motor FLA is 6.5 amps. I do not own a clamp on meter yet but may have to buy one. The motor is 3 phase and claims 2kw but says HP so either 2 or 2.5 hp. Pony is 5hp.

Should the thermal overload relay not be sized bigger? Does anyone know running amps of a 2hp 3phase motor not under full load? This lathe came from a school and I did find loose wiring in some spots. Could this be wiring gremlins? The twist lock plus seems kinda loose and wonder is current loss could be there?
 

Attachments

  • IMG_4021.jpeg
    IMG_4021.jpeg
    2.1 MB · Views: 10
Last edited:
CEC 28-306 Rating or trip selection of overload devices

...if of the adjustable type, shall be set to trip at not more than the following:

a) 125% of the full load current rating of a motor having a marked service factor of 1.15 or greater; or

b) 115% of the full load current rating of a motor that does not have a marked service factor or where the marked service factor is less than 1.15.
 
The one caveat to Rule 28-306 is found in Appendix B of the CEC:

The manufacturer's instructions should be consulted to determine how to match the trip setting or rating information to the full load current rating.
 
Here’s the data sheet for a typical Baldor 2HP 230/460 3-ph motor. Full load rating is 5.6A @ 230 volts. The bottom chart is for 460 volt, double the current draw for 230 volt.

IMG_0051.jpeg
 
In the example @whydontu gave, the manufacturer already gives the S.F. (service factor) amps to be used for determining the overload settings at each voltage.

S.F. = FLA @ 230 V = 5.6 = 6.3/5.6 = 1.125 <- so this specific motor's S.F. is 1.125 vs 1.25 or 1.15.


@Hollow-Grind

If your motor's nameplate doesn't give the already calculated S.F. Amps then you would follow the CEC rule as shown above to determine the overload setting.
 
I will assume the relay is stock. It only adjusts to 4amps but motor FLA is 6.5 amps. I do not own a clamp on meter yet but may have to buy one. The motor is 3 phase and claims 2kw but says HP so either 2 or 2.5 hp. Pony is 5hp.

Follow what elektrishun has posted. AS you can not adjust to that level then you will likely need a new overload and make sure that the contactor can also handle the increase in current.

If your building this type of project it is a good idea to borrow or buy a decent clamp on meter as you may have a high leg or some other anomalies in your build.
This is the one I recommend to my budget minded apprentices. https://www.homedepot.ca/product/kl...r-ac-auto-ranging-400amp-with-temp/1001545933
 
Thanks for all the advice. It just bothers me that this was probly designed to work the way it is and I can’t make it yet. I will buy a clamp on meter to test with. Rona plus has a Fluke for half price 🙂


Pic of lathe motor name plate for reference.
 

Attachments

  • IMG_4024.jpeg
    IMG_4024.jpeg
    1.6 MB · Views: 6
Bought a cheap clamp on Fluke meter and it arrived today. Should have bought one sooner. I’ve played with caps but can’t get the amps down. Best I can do is T1 5.1 amps, T2 4.9 amps and ghost leg 4.2 amps. Voltages under lathe load are T1-Ghost 235, T2-Ghost 245, T1-T2 244

Adding caps just up’s the amp load. Currently I only have 70 and 35 UF caps to play with. Still well under the 6.5 FLA nameplate of the lathe motor but over the 4 amp thermal overload.

Not throwing in the towel yet…
 