Can you share some technical details of the system in the picture above?
Hardware?
Cost?
Battery life expectancy?
Are those inverters parallable on the secondary?
Assuming the main breaker box is isolated from the utility, and the overall load is kept below the inverter(s) rating, and only a handful of the branch circuit breakers were closed for ease of power distribution around the house, would those inverters be okay with the impedance of the distribution via the panel?
Knowing what you know now after assembling this, would you do the same now?
I have a generator but it would be nice to have a silent backup for short outages. I don't imagine our power reliability is going to improve any time soon.
Our neighbor a few doors down has a serious backup generator that runs on natural gas about the size of van looks like it would be for grocery store or hospital. Middle of a snow storm and simultaneous winter power outage and his heated driveway is steaming away, Christmas lights on. Power outage? Oh we didn't notice.
The system originally started with ELCON battery chargers controlled via J1939 CAN messaging to charge Lead Acid Batteries. The batteries were recharged with an ONAN diesel genset. There was also solar panel charging. The generator was started and stopped automatically. This photo shows the big batteries and the starting battery. Under the 'table' is a power supply that was supposed to be for my CNC system to fake out solar cells. Solar controller beside that. On the 'table', two 1500W Elcon chargers, relays etc and on the far right my controller module.
When the system was changed to Lithium batteries and more reliable DeltaQ chargers some major changes had to happen.
There's a used charger on ebay for $250, new ones run over $1000.
The IC Series are compact, flexible, user-friendly industrial chargers that optimally charge lead-acid (wet, AGM, gel) and lithium battery packs to provide the best performance for the intended application.
delta-q.com
The inverter are MeanWell TS-1000 units.
They were scrapped for something else. Not sure what. Not privy to that information. And no they can't be paralleled which is really too bad.
The problem was that the military client didn't want to go through the entire testing and certification process on the software so instead I built a module that translated CANopen messages to J1939 messages. Now from the software perspective the 3 DeltaQ chargers look like ELCON chargers.
Now here's the problem with Lead Acid and why the change to Lithium.
1. Discharge below 50% State Of Charge (SOC) and reduce the life big time so the generator had to start at SOC 50%.
2. Lead Acid batteries take forever to reach 100% SOC and draw very little current during that time so the diesel generator would run for extra hours with almost no load. They would carbon up on their exhaust system
Lithium Batteries with their Battery Management System (BMS) can be discharged to 5% SOC without changing the number of discharge/charge cycles and can take full current (70A) up to 99% SOC. Only about 30 minutes at a final conditioning 10A is required to finish charging them.
Down side of Lithium batteries is temperature. Below -20C or so the BMS won't even enable the contactor and below zero or so charging is not allowed. So those systems, when it's that cold require the generator or shore power to start producing power to heat the batteries. Once they reach 5C the chargers are enabled and the batteries brought up to 100% and the application load is enabled. Once they are charged the generator is switched off and the battery controller runs the heat blankets to keep the batteries warm enough for for load discharge.
The control for the Lead Acid evenually had these modules.
One to control the generator including decoding flashing fault lights and measuring starting battery voltage etc. (Generator Interface Module -- GIM)
Another to deal with the lead acid battery charging voltages, current, temperature etc (Battery Interface Module -- BIM)
The small grey box has 5 CAN bus channels to talk to 3 sets of Lead Acid banks/chargers etc. It was originally developed to run thse 5 CAN bus channels; one for the north side and one for the south.