This is atypical. Most people wire 4 wires for 240.120V - transformers large enough (in history 200VA or better) normally aren't part of a normal installation, in my experience...I have actually few few machines that run 240 -> 120v transformer - I even use two such transformers to power a lamp.
This.Don't put a 3HP motor on a cheap 3HP VFD.
I installed a TECO 2HP for 2HP mill and Surface grinder - both are low load machines, even on startup. On higher load machines, such as a lathe, I'd be careful using a 2HP on a 2HP machine. It isn't much more money, even on a TECO, to get some extra capacity.For my lathe I went the TECO route as well, 2hp VFD on a 1.5hp motor, luv it.
I have a 1.5hp on my lathe and will replace it with a 2 hp. Likewise, when I converted my old mill I had a 1hp and went 1.5 for the 3-phase.It has a 1.5 hp...what would be a big enough motor....
I actually have almost no 1ph machines, certainly no large machines other then the compressor - all are 3ph so 3 wires + 1 ground. Almost all these machines have transformers for control voltage, either 120v or 24v. Usually the transformer is large - 100Va or bigger. Most transformers have more then one tap, some have three - 240, 480, 600.This is atypical. Most people wire 4 wires for 240.120V - transformers large enough (in history 200VA or better) normally aren't part of a normal installation, in my experience...
2Hp or even 2.5Hp is plenty on a lathe that originally had a 1.5 HP motor. Just make sure you set a suitable spin up time on your VFD so the bigger motor spins up slower than it could if left to its own. This will make sure the gears and bearings in your lathe are not overly stressed.It has a 1.5 hp...what would be a big enough motor....
I had read about up sizing the VFD and talked to emotors and they recommended the 2hp VFD for the 1.5hp motor.
Teco makes 1 hp VFDs. I had one on my surface grinder.That's because TECO doesn't make a 1.5hp VFD to my knowledge. Always go up on the VFD, never down.
Didn't say they don't make 1HP. I said no 1.5HP. The L510 comes in 1 ,2, & 3HP. No 1.5.Teco makes 1 hp VFDs. I had one on my surface grinder.
eMotors Direct - Canada's Online Source for Electric Motors, Gearing, and Controls
www.emotorsdirect.ca
It should be noted that there are two different standard wiring layouts for 3 phase - Y and delta. Y has 4 conductors plus a ground. Delta has 3 conductors plus a ground. In the Y configuration, in theory, the central neutral carries no current. In practice it has to be double sized because it carries transient currents causes by imbalanced loading in the phase circuits. Delta wiring is more common especially for longer distancesI actually have almost no 1ph machines, certainly no large machines other then the compressor - all are 3ph so 3 wires + 1 ground. Almost all these machines have transformers for control voltage, either 120v or 24v. Usually the transformer is large - 100Va or bigger. Most transformers have more then one tap, some have three - 240, 480, 600.
It feels smaller 3ph machines try to avoid transformers - like say pedestal grinders or two small drill presses I now have.
Whoops sorry!Didn't say they don't make 1HP. I said no 1.5HP. The L510 comes in 1 ,2, & 3HP. No 1.5.
But I also said, "as far as I know". Maybe they do on a different model.
Like @YotaBota , TECO told me to put a 3hp VFD on my 2.4hp motor.
I'd like to add that the vast majority of motors you will see* are delta wound.It should be noted that there are two different standard wiring layouts for 3 phase - Y and delta. Y has 4 conductors plus a ground. Delta has 3 conductors plus a ground. In the Y configuration, in theory, the central neutral carries no current. In practice it has to be double sized because it carries transient currents causes by imbalanced loading in the phase circuits. Delta wiring is more common especially for longer distances
My first 3PH wiring job (45+ years ago) was to fix a rotary phase converter installation. The licensed, bonded, 'master' electrician had wired it up so when the lathe was turned on 2 of the 3 power capacitors blew up, or rather burst, and the third was overheated. Knowing the difference between delta and Y configurations was the key to fixing it.
* except for 208V 3PH - I've seen a few in my time...