• Scam Alert. Members are reminded to NOT send money to buy anything. Don't buy things remote and have it shipped - go get it yourself, pay in person, and take your equipment with you. Scammers have burned people on this forum. Urgency, secrecy, excuses, selling for friend, newish members, FUD, are RED FLAGS. A video conference call is not adequate assurance. Face to face interactions are required. Please report suspicions to the forum admins. Stay Safe - anyone can get scammed.

Adding an emergency stop button on 3 phase motor, yes or no

RickyD

Member
Hi Guys,
I was wondering after modding my mill and also my lathe to VFD and 3 phase motor, if I should add an emergency STOP button, in case something goes wrong.
I guess, a big red button that would cut the 3 phase current going to the motor. I saw that removing current to the VFD, leave it ON for a couple seconds before it shut down so it's not quick enough. Also, finding and pressing the small STOP button on the VFD is not practical in case of real emergency.
So my question is: Can it damage the motor to suddenly cut the 3 phase power going to it ?
Do you have better solutions for achieving that?
Thanks !!
 
Your VFD should support a low voltage ESD function. Use that. Killing the 3phase between the VFD and motor is not recommended.

ESDNew.JPG


In this picture the LV ESD is on the left. LV FWD/REV/STOP is on the right and the metal ON/OFF sw is for power to the the VFD.
 
Last edited:
Ok, I understand, and thanks for you comments... I believe my VFD does not have a low voltage control built-in. It requires an optional IO board.
I have the KBDA-27D
I will try to find a way, or get the IO board.
 
General question - does the VFD stop the motor abruptly when this LV eStop is used?

If not, would the addition of an active shaft brake make sense ?

Asking for a friend
 
Last edited:
General question - does the VFD stop the motor abruptly when this LV eStop is used?

If not, would the addition of an active shaft brake make sense ?

Asking for a friend

No, mine just free wheels to a stop, but I don't have a braking resistor either.
 
Last edited:
Looking at the KBDA manual, table 12 on page 26, it appears to have a 28 position terminal block with various ways to initiate a STOP.
Page 19 references injection braking.
 
Ok, I understand, and thanks for you comments... I believe my VFD does not have a low voltage control built-in. It requires an optional IO board.
I have the KBDA-27D
I will try to find a way, or get the IO board.
wow that is insane, over $600 bucks for the VDF and if doesn't support I/O without an aux board that costs another $150.

In your case though, I'd buy it, because if you wire the motor or the VFD into the e-stop you lose all possible braking. You paid a lot for the feature, so why eliminate it in case of emergency
 
I just purchased another used 2HP Altivar with Sensorless Flux Vector control and external braking, this one was $70 on eBay. I have three used Altivar's now. All work perfectly. The only bad VFD I have experienced was purchased new and failed IIRC with < 10 hours of actual use but beyond the return period from the big river store. I'm sticking to name brands with: certifications, SLV and external braking.

A little FYI about certified vs. non-certified products. Beyond the obvious safety aspect, there are a number of EMC tests performed to verify that the device:
1) Does not radiate excessive electrical noise that will disturb adjacent electronics
2) Can withstand electrical transients that typically occur during electrical storms and switching on/off of motors etc.

These tests require expensive test equipment and some expertise however they quickly demonstrate the failure modes of poorly designed equipment. We fixed products that were being sold for years that would for the most part make it past the warranty period, but where by no means "reliable". We could blow them up 100% of the time with one simple fast transient or combo wave test within seconds. The lucky end users were simply using them in a more benign environment. With just a little bit of additional filtering in just the right location, we could run these tests over and over with no failures. So often that name brand product with the extra $10 worth of components is better value even if it cost $200 more.
 
Last edited:
In the case of normally open fwd/rev switches, ie non momentary (drum switch, apron switch), the e stop can be wired in series and will initiate braking just as if the regular switch was turned off. Even momentary switches can be wired in a similar fashion but the e stop would become its own input and braking would be programmed separately.
 
My 3 phase mill and lathe both have an Emergency stop button connected to the low voltage bus. Mill has DC injection braking, and lathe has resistor braking. The E-stop puts the brake on on both machines.
I would get a VFD from Vevor and put your 600 dollar box up for sale. You could buy 3 of them for what you paid for that thing.
 
My 3 phase mill and lathe both have an Emergency stop button connected to the low voltage bus. Mill has DC injection braking, and lathe has resistor braking. The E-stop puts the brake on on both machines.
I would get a VFD from Vevor and put your 600 dollar box up for sale. You could buy 3 of them for what you paid for that thing.
I guess, since I would have to sell it probably for half price, and buy another one... I would be better to get the IO module for 150$, and learned from that for next time...!
Thanks !
 
I guess, since I would have to sell it probably for half price, and buy another one... I would be better to get the IO module for 150$, and learned from that for next time...!
Thanks !
exactly, the resale value on quality VFDs is not strong, so you're better keeping it and getting the I/O board IMO.
 
I just have an intermatic brand one. Takes 5 minutes to install, just shut your main off first.
We had a lightning strike here about 10 years ago, it took out Microwave, Washer, Furnace control panel, anything electronic not on a surge protector not wanting to go through that again.
The worst part is you had to pay the repair man to pronounce stuff dead and that cost was taken off your payout.
 
We had a lightning strike here about 10 years ago, it took out Microwave, Washer, Furnace control panel, anything electronic not on a surge protector not wanting to go through that again.

The bad news is that they are not a 100% solution. The big lightning strikes just fry the protector and then move on to fry everything downstream too.

I've learned to use them but install other protection too. I put a big piece of pipe with a pointed rod on that at the top of my Radio Tower and then ran big braided ground wire to three 6ft grounding rods driven into the ground. I installed a premium protector between the tower and house. Lightning still manages to fry my router and entertainment center on a regular basis. The basic problem is major lake effect storms that build up huge charges out over Lake Erie and then discharge it at the Glacial Ridge my home is built on.
 
The bad news is that they are not a 100% solution. The big lightning strikes just fry the protector and then move on to fry everything downstream too.

I've learned to use them but install other protection too. I put a big piece of pipe with a pointed rod on that at the top of my Radio Tower and then ran big braided ground wire to three 6ft grounding rods driven into the ground. I installed a premium protector between the tower and house. Lightning still manages to fry my router and entertainment center on a regular basis. The basic problem is major lake effect storms that build up huge charges out over Lake Erie and then discharge it at the Glacial Ridge my home is built on.
Good to know. We have grounding rods because we aren’t on city water, house and shop building.
 